Interpretation of Net Allowable Bearing Pressure
ptdgeo
Geotechnical
Dec 13, 2007
20
I realize this topic has appeared and been discussed here many times, but for myself I would like to bring it up one last time to assure myself I’m thinking correctly when explaining this topic to fellow structural engineers that call regarding this question.
Most recently I had a site that was in a valley setting where the soils at the site were alluvial deposits composed of a sequence of fat clay, lean clay and sand over shale. The fat clay had formed a desiccated crust over the underlying lean clay, that was normally consolidated to just slightly overconsolidated, and the sand below was medium dense to dense.
The structures for the project consisted of a single story mechanical building and reinforced concrete sedimentation basin with 20’ tall walls and a concrete roof. The floor slab for the mechanical building needed to be a minimum of 5 feet above grade for flood protection.
Long story short, total settlements needed to be less than 1 inch and an increase in the vertical effective stress greater than 300 psf calculated more than an inch of settlement. The client did not want to use deep foundation or any type of ground modification technique because the “local” contractor wasn’t equipped to handle them.
We ended up giving recommendations for “contact” pressures for a mat foundation established at depths ranging from 5 to 10 feet below the existing ground surface with anticipated total settlements of 1 inch or less. I used the term “contact pressure” because the structural engineer and I could not agree on the meaning of “ net allowable bearing pressure”.
The structural’s argument was, that if bottom of the mat was at 10 feet below existing grade, then he could use the net allowable pressure I was giving and add the weight of the soil removed. His explanation, “you give a net allowable pressure of 1500 psf for a mat at 10 feet deep, so to size the mat I can use at least 2500 psf, by taking advantage of the soil removed.” My reply was, “No, not if you want to keep settlements to less than 1 inch.” So I was informed that I was not giving him a “net allowable pressure” because a net allowable pressure is that pressure in excess of the overburden. I agreed, with half of his statement, and explained myself by saying:
“A net allowable bearing pressure is that pressure in excess of the overburden and it does account for the depth of overburden but what that means is that this is the total change in effective vertical stress that the soil below the foundation can experience to keep settlements within serviceable limits. The 1500 psf is the 10 feet of soil (gamma total 120 pcf) plus the 300 psf increase in effective stress at that depth. So this pressure is what needs to be used to size foundations and should be the total of the structures dead load and live load divided by the given pressure.”
After a little more banter, back and forth, regarding the meaning and definition of bearing capacity versus settlement and that the strength of the soil was not the issue because from a bearing capacity standpoint the soil probably could support 2500 psf without a bearing failure but it was the soil’s compressibility characteristic that was governing, so we agreed to use the term “contact” pressure.
My question is, does that make sense? Even if I were to have called the term a net allowable pressure of 1500 psf, technically wouldn’t that have been correct? By the structural's interpretation the net allowable bearing pressrue should have been 300 psf., I didn't agree.
Sorry about the long message.
Regarding misinterpretations of the geotech report; the geotechs in my area almost always say "allowable bearing pressure" and don't state if it is a "gross" or a "net". Usually when I ask they say they meant net, but I wish they would just state that to begin with.
panars - I'll be in Indiana in January - can we get together, maybe? with Jeff? I understand your point for clarification - but note that you use the terms nominal resistance and factored resistance. Goes along with capacity. So, I've calculated the LRFD resistances and all that - everything is copacetic. But, you do a settlement analysis (say using Hough if so inclined) and the settlement is 50% larger than permitted by the requirements of the structure. What good is the factored and nominal resistances now? We must develop a safe pressure that the settlement doesn't exceed. Does LRFD do this for me? For all those, it is true that we geotechs should use net in our "allowable bearing pressure" wording.
BigH- Settlement in LRFD (Load and Resistance Factor Design) is a service limit state, and as such it uses unfactored loads. As the geotech, you would calculate the bearing resistance for the service limit state (controlled by settlement) and the factored bearing resistance for the strength limit state (controlled by failure of the soil). It will then be up to the structural engineer to determine which controls the footing design (or you can do it if the structural engineer will give you the dead load, live load, wind load, earthquake load, etc.). I realize this overlooks the effect that footing size has on settlement. This can be addressed by presenting a graph that correlates settlement with footing size for a given bearing resistance.
I'll contact you off-board about January.
We don't need new clarifying terms. The clarifying terms already exist. See Article 7,3 in Bowles 4th Edition:
Net Pressure - pressure in excess of existing overburden pressure, based on settlement considerations.
Gross pressure - total pressure whch can be carried, based on bearing capacity.
Whether the pressure is a gross or net value should be stated in the geotech report, but often, is not.
In this case, the geotech report should have given the allowable bearing pressure as 300 psf net pressure.
miecz
Interesting. That is the same argument/disagreement interpretation issues I had with the original SEOR. You’re not him are you???
Funny after all the above comments it comes around full circle again.
ptdgeo
Well, I guess I'm in total agreement with your SEOR. After reading the 9 pages (printed 'em) of comments, I don't think your original question
was answered. My position is no, it should have been a net allowable pressure of 300 psf.
BigH
Yes, if the allowable pressure is based on settlement, then the soil report should say net allowable bearing pressure. If the allowable bearing pressure is based on bearing capacity, then the soil report should say gross allowable bearing pressure.
This is getting confusing - I have always understood the geotechnical terms "net" and "gross" to deal with the types of loads included in their use, not on what the limit state of the design was.
From my earlier post - the key is for you geotechs to simply be sure you communicate your intent, and that the intent is correctly understood by we thick skulled structurals.
miecz
First I hope my comment, "you're not him are you??" was taken in good fun - that is the way it was intended anyway.
Second, you are correct that nobody, besides yourself, directly answered my question in the OP.
Third, and this ties in with JAE's latest post, I have always intended for a "net" allowable pressure to deal with the type of loads that should be included (i.e. for "net" no need to include the load from the overburden, only the loads associated with the proposed structure need to be used)
ptdgeo-
Yes, your question made me laugh (and I need a good laugh).
From your latest post, it seems as though your definition of net pressure is the same as mine, i.e., it doesn't include the overburden (the excavation). If I understand your original post, then, the net allowable pressure is 300 psf.
We did get off track - and if 300 psf additional loading over and above the effective overburden pressure at the invert of the footing at the gives you the 1 inch settlement and this is the operative serviceability limit, then 300 psf is the net allowable bearing pressure that would be given. The designer could put a gross bearing pressure equal to the weight of the soil removed (divided by the footing area) plus 300 psf.
okay.
but say you are to give a footing pressure for a fully compensated mat foundation 10 feet in the ground and the total unit weight of the soil removed is 120 pcf
How would you term that pressure in a report?
Net allowable bearing pressure of 0 psf?
Allowable bearing pressure of 1200 psf?
Contact pressure of 1200 psf?
or something else?
ptdgoe-
I'm not sure what you mean by fully compensated. If the allowable is based on settlement, 1 inch in your original post, then there must be some net pressure that would cause that settlement.
JAE-
In terms of "limit states", I think the terms "net" and "gross" are directly related to the design limit state; net loads are used for the deflection (settlement) limit state, and gross loads are used for the strength (bearing) limit state.
miecz - yes both HAVE limit states, but the terms net and gross have always distinguished between whether you include existing overburden or not.
Net has always meant to me (and to most textbooks on foundations) as a difference in pressure that the soil feels due to the footing while Gross has always meant the total pressure, regardless of whether it is the original overburden pressure or the newly added foundation pressure.
From Ralph Peck's Foundation Engineering: [blue]"The net ultimate bearing capacity is defined as the pressure that can be supported at the base of the footing in excess of that at the same level due to the surrounding surcharge".[/blue]
To say that NET means one type of limit state and GROSS means a different limit state isn't what I've seen and used for 30 years. News to me.
miecz
a compensated foundation, also referred to as a floating foundation, is a foundation that is designed and constructed by excavating a volume of soil with a weight nearly equal to that of the proposed structure and then constructing the foundation in the bottom of the excavation, thus the increase in vertical effective stress in the soil, is very small. For a fully compensated foundation the loads from a structure would equal the weight of the volume of soil removed, resulting in a zero change in stress. However, there are rebound concerns, buoyancy concerns with groundwater issues, and the live load varies over time so the weights are not always perfectly balanced.
so from my latest post above, curious how folks would term the pressure to put in a report for a SE to use for sizing this type of foundation
for anyone's interst on buoyancy foundations - see Tomlinson's book on Design and Construction of Foundations and Chapter 12 by H.Q. Golder in Winterkorn and Fang's Foundation Engineering Handbook, 1st Edition.
If there are any code specifiers out there and professors - perhaps you should all be more concerned with the concerns raised herein than by 4th order FEM analyses using 1st order soil parameters.
I'm feeling really thick here, as I'm having trouble understanding where we disagree. So let me back up a bit. I don't believe that disagree on the definition of net pressure, or that net pressure is what causes settlement. I don't believe we disagree on the definition of gross pressure or that gross pressure is what would cause a bearing capacity failure.
When the op asks: "if I were to have called the term a net allowable pressure of 1500 psf, technically wouldn’t that have been correct?", I don't think we disagree that a net allowable pressure of 1500 psf is incorrect.
So, I guess the disagreement is in the standard practice. If you'r saying that geotechs don't specify allowable net pressures to direct the engineer to use net pressures, and allowable gross pressures to direct the engineer to use gross pressures, well, even the author (Bowles) says it's not often done this way, so I'd have to agree with you there.
What I was saying, is that it should be done that way, as, it's clear and easy, and, no other proposed system makes sense to me.
Sorry, the above post should have been addressed to JAE.
Okay Bearing and settlement are like beer and ice cream, both are great, just not together.
Gross bearing pressure is the total pressure that will cause a shear failure of the foundation. Net bearing pressure is the gross bearing pressure less the overburden stress.
Settlement is due to additional contact or applied stress above the existing overburden stress and represents compession of the underlying soil due to elasyicity(sands) or drainage (cohesive soils) Peck devloped the charts that combined the two concepts and they have been hopelessly linked ever since.
To make the matter simple, tell the structures guy what he wants to know: the foundation is 10 feet deep and can have an applied stress from the structure of 300 psf.