Intertrip/Interlocking between IED which using different communication protocol

Status
Not open for further replies.

bee79

Electrical
Mar 11, 2015
24
MY
Dear Experts,

As per the subject, if an upstream IED using Modbus and downstream IED using IEC61850 communication, how to implement the intertrip/interlock function between them?

The upstream and downstream equipment are located very far from each other where hardwire connection is not possible and fiber optic is the only solution.
 
Replies continue below

Recommended for you

I am assuming GOOSE messaging and that if the project specification was for IEC61850, then the speed of IEC61850 would be required. I don't know if there is a protocol converter.

Using two SEL-2505's would be the simplest and probably most economic solution if the Mirrored Bits communications would be acceptable.
 
I would do what jghrist recommended. Cheap, easy and effective.
 
Dear All,

Thanks you for your supportive answers. I have few options now and will choose the most economical solution when finalize the design.
 