freetown
Electrical
- Mar 1, 2024
- 18
Hi all,
We recently installed a Liquid Resistance Starter in replacement of grid rotor resistance for 2 motors 11kV/2700kW.
With grid rotor resistance, we could make a rotor to earth insulation test using Megohmmeter insulation tester (we test rotor+cables+resistances connected together). The value to earth we find can go from 500 M/Ohm to 1G/Ohm (with 500V test).
With liquid Resistance Starter when perform the same test (cable+rotor) we only find around 200 K/Ohm. We thought that there is a problem on cables or rotor, but when disconnect cables of Liquid Resistance Starter contactor and testing cable+rotor we find the normal value (500 M/Ohm to 1G/Ohm).
The motor is running without problems, according to the manufacturer the value we found (K/Ohm) when testing is normal. It’s because of liquid and moving electrodes.
My question is it normal we find this small value between rotor to earth and what’s the exact reason for this value?
Every time when want to test rotor, we have to disconnect cables from liquid Resistance Starter contactor, is there a way to test the rotor without disconnecting cables as for grid rotor resistance?
We want to measure rotor current, is there a device allow us to measure current and torque of the rotor in real time?
Thanks.
We recently installed a Liquid Resistance Starter in replacement of grid rotor resistance for 2 motors 11kV/2700kW.
With grid rotor resistance, we could make a rotor to earth insulation test using Megohmmeter insulation tester (we test rotor+cables+resistances connected together). The value to earth we find can go from 500 M/Ohm to 1G/Ohm (with 500V test).
With liquid Resistance Starter when perform the same test (cable+rotor) we only find around 200 K/Ohm. We thought that there is a problem on cables or rotor, but when disconnect cables of Liquid Resistance Starter contactor and testing cable+rotor we find the normal value (500 M/Ohm to 1G/Ohm).
The motor is running without problems, according to the manufacturer the value we found (K/Ohm) when testing is normal. It’s because of liquid and moving electrodes.
My question is it normal we find this small value between rotor to earth and what’s the exact reason for this value?
Every time when want to test rotor, we have to disconnect cables from liquid Resistance Starter contactor, is there a way to test the rotor without disconnecting cables as for grid rotor resistance?
We want to measure rotor current, is there a device allow us to measure current and torque of the rotor in real time?
Thanks.