Hello,

I read that irig-b resolution is 10 ms but actual timecode generators usually have a resolution better than 1 µs.

I'm looking for some elaboration on this since I do not understand. Does the 10 ms resolution mean that the actual time provided by irig-b error could be up to 10 ms off from actual time? If so, would the 1 µs resolution apply in addition the to existing error?

Also, I'm not sure if this is the best place to ask but I thought I would throw it in since there is not a lot of information on the web on irig-b. If anyone has a recommendation for a low-cost irig-b signal generator, please let me know. I am not concerned with the actual time value being correct but I would like to have an irig-b signal on a coax line to work with. I've been watching generators on ebay but am hoping to find something in the sub-$100 price range.

Thanks.
 
Replies continue below

Recommended for you

?? The very first hit in Google is the specification for IRIG STANDARD 200-98

TTFN
faq731-376
7ofakss

Need help writing a question or understanding a reply? forum1529


Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com:
 
Yeah, saw that spec, if it answers my question I didn't catch it.

I didn't actually have the question until I was a bit further down the list. Hit #36 for "irig-b resolution" Google search was one of your posts here from 2002, IRstuff. I'm hoping you can help me with my confusion...

If IRIG-B resolution is 10 ms, and a timecode generator resolution is 1 ns, does that mean that each pulse will be +/- 1 ns after the previous pulse but the timecode data on each individual pulse may be +/- 10 ms due to the IRIG-B resolution itself?
 
"Does the 10 ms resolution mean... ...up to 10 ms off from actual time?"

First thing is to distinguish between resolution and accuracy. A time signal can be low resolution yet extremely accurate. For example a simple 1 pps pulse train only identifies time to the nearest second resolution (referencing absolute time using other more informative references), but often does so to extremely high accuracy (perhaps within a us).

For the code resolution, start with Wiki (but check it against better references). It states "...Typical commercial devices will synchronize to within 1 microsecond using IRIG B timecodes."

Once the client (slave) device has synchronized, it can itself break up absolute time into finer units. Just like setting your watch to the dropping ball in Greenwich.
 
Thanks for pointing out my misunderstanding VE1BLL.
 