Is a Resistance-grounded system still considered 347Y/600?

Status
Not open for further replies.

tumbleweed1

Electrical
Sep 19, 2013
44
Looking at ratings on some motor protection circuit breakers, they have ratings for say, 277Y/480 or 347Y/600. If we have a low voltage generator with resistance grounded neutral, it's not considered a delta system really, but we also wouldn't consider it a 277Y/480 correct? So in effect, these MPCBs cannot be used on a resistance grounded Y system- is that right?
 
Replies continue below

Recommended for you

That's correct. As far as ratings of that sort are concerned there's solidly grounded and there's everything else. Your resistance grounded system falls into the everything else category.
 