imisspla07
Electrical
- Mar 11, 2010
- 13
I have a power factor correction capacitor bank rated 600kVAR. It is in parallel with three 1250hp motors on soft start systems used for gas compression. The bank has a contactor that closes only when 2 or three motors are running and is unlatched when the soft start is ramping up the motors. So, basically, it is only latched in when 2 or 3 motors are running full speed. The first time we used the cap bank it blew the fuses upstream of the contactor (connected to the bus). We changed out the fuses to different fuses and the second time it ran it blew the cap bank. It was suggested we have harmonics issue, but the utility did a power quality study and showed .05% harmonics. Seems low to me. Also, it was mentioned it might be resonance. But when I went out there with the utility we only latched in 300kVAR; half of the full amount. This should have gotten us away from any resonance issue. Now, the last thing to note is that when we did latch in the 300kVAR, it made a very eerie sound, like someone was waving a light saber in front of you (wa, wa, wa, wa). Definitely didn't sound right, so we latched it back out. I have no idea what's going on with this thing. It's been noted maybe it's from the utility. Someone mentioned perhaps an open NGR at the utility. Any ideas would be GREATLY appreciated!