I know it's not commonly done but is it acceptable according to the Canadian Electrical Code (or American Electrical Code) to connect live wires to the bottom instead of the top of a non-fused rotary disconnect switch (Socomec model 27003021; Link to website: ) inside a control cabinet if it is used a disconnecting means for that control cabinet and is door interlocked? This would make the routing of the cables into and out of the cabinet easier and cheaper. A finger guard would be installed on the bottom of the switch where the live wires are connected and I would put a sign on the outside of the cabinet door.
The only reference I could find in the 2021 version of the Canadian Electrical Code (CSA C22.1:21) was section 14-506 Connection of switches.
14-506 Connection of switches
Manual single-throw switches, circuit breakers, or magnetic switches shall be connected so that the
blades or moving contacts will be dead when the device is in the open position, except that the
following need not comply:
a) branch-circuit breakers that have all live parts other than terminals sealed and that are constructed
so that the line and load connections can be interchanged;
b) switchgear that is provided for sectionalizing purposes and has a suitable caution notice attached
to the assembly;
c) switches that are immersed in a liquid and have a suitable caution notice attached to the outside
of the enclosure;
d) switches that are designed so that all live parts are inaccessible when the device is in the open
position; and
e) magnetic switches, when preceded by a circuit breaker or manual switch that is located in the
same enclosure or immediately adjacent and is marked to indicate that it controls the circuit to the
magnetic switch, unless this is obvious.
I think condition d) applies to this situation as all the live parts are inaccessible when the device is in the open position.
Thanks in advance
The only reference I could find in the 2021 version of the Canadian Electrical Code (CSA C22.1:21) was section 14-506 Connection of switches.
14-506 Connection of switches
Manual single-throw switches, circuit breakers, or magnetic switches shall be connected so that the
blades or moving contacts will be dead when the device is in the open position, except that the
following need not comply:
a) branch-circuit breakers that have all live parts other than terminals sealed and that are constructed
so that the line and load connections can be interchanged;
b) switchgear that is provided for sectionalizing purposes and has a suitable caution notice attached
to the assembly;
c) switches that are immersed in a liquid and have a suitable caution notice attached to the outside
of the enclosure;
d) switches that are designed so that all live parts are inaccessible when the device is in the open
position; and
e) magnetic switches, when preceded by a circuit breaker or manual switch that is located in the
same enclosure or immediately adjacent and is marked to indicate that it controls the circuit to the
magnetic switch, unless this is obvious.
I think condition d) applies to this situation as all the live parts are inaccessible when the device is in the open position.
Thanks in advance