Folks:
We have just installed metering on a 46kV class subtransmission line with vertical configuration. We assumed the phase layout was A-B-C top to bottom but it turned out to be B-C-A. There is no neutral so we used two element metering, connecting the VT primaries B-C and A-C making the common point of connection between the voltage transformers the middle (C) phase. We put the CTs in the top and bottom phases (B and A). So we have the usual 120 degree currents and 60 degree voltages one would expect for delta metering. And we have the correct phase rotation.
But the client is unhappy saying the installation is not "standard" since the terminals on the test block, and on the drawings, labeled A are actually B, etc. It will cost big bucks to reconfigure the primary connections.
In my experience the choice of labelling of phases in metering is arbitrary and makes no difference to the meter readings. When I look in IEEE Standard C57.13 the diagrams (pgs 32 -37) do not label the phases so I would assume labelling is arbitrary.
Would anyone know of a standard or industry reference that states clearly whether labeling of phases for metering is arbitrary or not?
We have just installed metering on a 46kV class subtransmission line with vertical configuration. We assumed the phase layout was A-B-C top to bottom but it turned out to be B-C-A. There is no neutral so we used two element metering, connecting the VT primaries B-C and A-C making the common point of connection between the voltage transformers the middle (C) phase. We put the CTs in the top and bottom phases (B and A). So we have the usual 120 degree currents and 60 degree voltages one would expect for delta metering. And we have the correct phase rotation.
But the client is unhappy saying the installation is not "standard" since the terminals on the test block, and on the drawings, labeled A are actually B, etc. It will cost big bucks to reconfigure the primary connections.
In my experience the choice of labelling of phases in metering is arbitrary and makes no difference to the meter readings. When I look in IEEE Standard C57.13 the diagrams (pgs 32 -37) do not label the phases so I would assume labelling is arbitrary.
Would anyone know of a standard or industry reference that states clearly whether labeling of phases for metering is arbitrary or not?