There are some easy tell tale signs such as: Does the column have stiffeners at the connection? Are there any doublers plates? Does the design drawings has any indications as to the connection type?
Having said that, you can go about this one of two ways:
1. If I were you, I would assume it is shear connection. This is conservative.
2. If you are at a point where member stresses are exceeding the allowable or you want to justify increasing load-carrying capacity, you can assume a moment connection. However, you must define the end fixity in percentages terms. If the flanges were full pen welded, then you would have a full moment connection. If it is not, you are in no man land! Your guess would be as good as anyone else. There are mathematical procedures that you may want to follow to determine a percent fixity; but is it worth it? I would say no. Plus you have to evaluate the column and see if it is adequate for the moment etc.
Be conservative like me and assume a pinned end condition.
Good luck