fb599
Electrical
- Oct 25, 2001
- 32
We have an island utility system of nominal load of 45MW. We are also connected via a 100km 90 kV AC cable link. During the summer months we do not run any generation, therefore we are hanging on this long length of cable. We use shunt/series reactors so that we balance out the capacitive reactance of the link. However, during light load periods (ie night time) we have to switch in 11 kV capacitors to balance reactance and nominal system voltage back to 11 kV. My Question is this, when we switch in the cap's, which are 3.15 MVAR and which in addition are connected in series with inrush reactors of 0.05mH the 11kV network suffers from large voltage transients. My phone hasn't stopped ringing since we went solo on the link ! We have tried to reduce sys. volts before closure and raise volts prior to opening the Cap. circuits but the effect obviously is still there for all to see. Is there a way of calculating the size of inrush reactor to reduce this voltage transient or do I need to rethink the whole VAR compensation issue with regard to HV Capacitors. FYI we have 6 of these units based at the power plant. Any help gratefully received. Otherwise I can't wait till winter when we start generating in parrallel again !.......