Good Morning/Afternoon/Evening to All,
I am inquiring as to some guidance on testing precautions and feasibility. The Generator under testing conditions is a G.E. LM2500 rated at 25 MVA, 13.8 kV, and 0.85 P.F. It has a Basler DECS-200 AVR system and we are looking to test its capability as a stand-alone unit by using a load bank configuration with different load profiles. The peak of the profile would be to attempt to simulate what would be a large inductive motor DOL starting such as a boiler feed pump rated at 1750 HP, 4000V, and 225 FLA with a continuous 3 MVA load already applied that experiences a peak of 10 MVA due to in rush from the boiler feed pump starting.
My question involves around the feasibility of this testing. The generator is being tested in its AVR condition which I believe to be its isochronous mode. It normally is operated in droop mode. I don't doubt the generators capability of supplying the intended load in a continuous fashion but I am questionable of the generator in a stand-alone setting experiencing large inductive motor starts. Unfortunately, the unit is very old and there is lack of performance data or even reactance values on hand.
What kind of information should be acquired before administering such a test?
What kind of precautions should be taken when applying loads to the generator in steps? To simulate a motor start, I would imagine using something along the lines of a step function where VA is high with low power factor at start and then incrementally raise power factor as VA decreases as the motor speeds up to operating condition.
How would you go about determining if the excitation system within the generator is capable of handling motor starting scenarios?
Thanks.
I am inquiring as to some guidance on testing precautions and feasibility. The Generator under testing conditions is a G.E. LM2500 rated at 25 MVA, 13.8 kV, and 0.85 P.F. It has a Basler DECS-200 AVR system and we are looking to test its capability as a stand-alone unit by using a load bank configuration with different load profiles. The peak of the profile would be to attempt to simulate what would be a large inductive motor DOL starting such as a boiler feed pump rated at 1750 HP, 4000V, and 225 FLA with a continuous 3 MVA load already applied that experiences a peak of 10 MVA due to in rush from the boiler feed pump starting.
My question involves around the feasibility of this testing. The generator is being tested in its AVR condition which I believe to be its isochronous mode. It normally is operated in droop mode. I don't doubt the generators capability of supplying the intended load in a continuous fashion but I am questionable of the generator in a stand-alone setting experiencing large inductive motor starts. Unfortunately, the unit is very old and there is lack of performance data or even reactance values on hand.
What kind of information should be acquired before administering such a test?
What kind of precautions should be taken when applying loads to the generator in steps? To simulate a motor start, I would imagine using something along the lines of a step function where VA is high with low power factor at start and then incrementally raise power factor as VA decreases as the motor speeds up to operating condition.
How would you go about determining if the excitation system within the generator is capable of handling motor starting scenarios?
Thanks.