Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

ITE breaker rating

Status
Not open for further replies.

kjjack

Electrical
May 1, 2002
12
0
0
US
Can anyone tell me where to find interrupt rating data for ITE 5kv HK model breakers?
 
Replies continue below

Recommended for you

From my EasyPower library data, there are three versions of HK breakers at 5 kV:

5-HK-75 (75 MVA)
5-HK-250(250 MVA)
5-HK-350(350 MVA)

If you can let me know what class you have, I can post the detailed ratings.

 
Hope this helps - I am basing this on our analysis software standard library data and I have not verified against any original ITE data, but I believe this data to be correct. Usual disclaimers apply. If anything doesn't look right, let me know.

Test Basis for both is ANSI-Symmetrical current basis.


5-AK-250:

MVA = 250 MVA
Nom kV = 4.16 kV
Max kV = 4.76 kV
K Fact = 1.24
Close & Latch = 58 kA
Interrupting Amps at Max kV = 30.3 kA
Max Interrupting Amps = 51 kA
Interrupting Time = 5 Cycles

5-AK-350:

MVA = 350 MVA
Nom kV = 4.16 kV
Max kV = 4.76 kV
K Fact = 1.2
Close & Latch = 78 kA
Interrupting Amps at Max kV = 42.5 kA
Max Interrupting Amps = 37.5 kA
Interrupting Time = 5 Cycles


 