buzzp
Electrical
- Nov 21, 2001
- 2,032
We have several older breakers type KC 1000 and KC 600, ITE breakers. We are upgrading our protective relaying for this facility. I am having difficulty finding 'make' requirements of the 'tripping coil' and 'pick-up coil' of these breakers. I do have the original mfg data and apparently, back in the day, 'make' requirements of inductive loads was not specified. The data sheets only state 'heavy contacts' should be used. I know the resistance of these coils but do not have any other information. I would like to get rid of the MG-6 relays which are carrying the load now and let the protective relay handle the load of the trip and pick-up coils. I am a little hesitant to do this due to the over designing which occurred with these older relays. The MG-6 will make 30A@575VAC with 12A continuous. Notice this is not a DC make rating. The new protective relay makes 30A per IEEE C37.90. My question is if anyone has any make requirements of these breakers? I know I could measure it with a scope but don't really want to take units down to run the test. Without this information I will be keeping the MG-6 relays. My experience with DC coils (hydraulics and pneumatics) says that these coils could be pulling up to 30 times there continuous rating when they are first energized. Any info or hindsight would be appreciated. Thanks.