JAE, I have a question about a post you made a couple of years ago. It is now closed so I can't put this question there. Can you help me understand your reasoning in Step 9 below on multiplying Sd x Ms and not fy/fs x Ms while using Phi=1? This has me hung up as I try to understand ACI 350 and how it bounces back and forth between service levels and factored levels.
Thanks.
JAE (Structural) 4 Jun 10 9:14
Jacst3,
Take a look at the attached mini-spreadsheet. This is an example of what we have used on a recent tank design.
Note that you use φ = 1.0 with the increased moment value from Sd.
The steps we would use are:
1. Determine the SERVICE moment in the member.
2. Determine the distance "a" which is the depth of the compression block under service loads.
3. Calculate the moment arm between the reinforcement and the center of the compression block (half-way across dimension a).
4. Calculate fs as the moment divided by the moment arm, divided by the area of reinforcement.
5. Calculate the maximum reinforcement stress, fs(max) from ACI 350 section 10.6.4. This is based on equations 10-4 or 10-5.
6. Verify that actual fs is less than fs(max).
7. Calculate the maximum permissible fs (fs(permissible)) from 10.6.4.
8. Calculate Sd using the fs(permissible)
9. Your design factored moment is your service moment times the Sd factor. No other load factors should be used.
10. Use your SdMs value with phi = 1.0.
You do get fairly large Sd values. But the key is to use more, smaller bars rather than fewer, larger bars to minimize the Sd.
Thanks.
JAE (Structural) 4 Jun 10 9:14
Jacst3,
Take a look at the attached mini-spreadsheet. This is an example of what we have used on a recent tank design.
Note that you use φ = 1.0 with the increased moment value from Sd.
The steps we would use are:
1. Determine the SERVICE moment in the member.
2. Determine the distance "a" which is the depth of the compression block under service loads.
3. Calculate the moment arm between the reinforcement and the center of the compression block (half-way across dimension a).
4. Calculate fs as the moment divided by the moment arm, divided by the area of reinforcement.
5. Calculate the maximum reinforcement stress, fs(max) from ACI 350 section 10.6.4. This is based on equations 10-4 or 10-5.
6. Verify that actual fs is less than fs(max).
7. Calculate the maximum permissible fs (fs(permissible)) from 10.6.4.
8. Calculate Sd using the fs(permissible)
9. Your design factored moment is your service moment times the Sd factor. No other load factors should be used.
10. Use your SdMs value with phi = 1.0.
You do get fairly large Sd values. But the key is to use more, smaller bars rather than fewer, larger bars to minimize the Sd.