Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Jockey Pump for Fire Pump system

Status
Not open for further replies.

tinotoro

Electrical
Nov 2, 2005
18
0
0
CA
Can the jockey pump be wired directly from the ATS in parallel with fire pump, or should it have a separate feed from power supply?
 
Replies continue below

Recommended for you

It COULD, but it would be unnecessary I believe. A Jockey Pump is there to keep the pressure up in the pipe due to leaks and such, but has nothing to do with the actual operation of the Fire Pump during a fire. That's not typically a function you would worry about during a short power outage.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 
Thanks for the answers, the feeder to the ATS is already installed with sufficient size to feed both. The MCC is far and want to avoid pulling a second cable. I wonder if NFPA 20 allows to use the ATS power supply for this.
 
If there is not a fire and a power outage your main fire pump is going to start every time the system leaks down a little. Your going to wear out the fire pump system by starting the whole system.
 
Status
Not open for further replies.
Back
Top