Just primary air for IT room cooling

Status
Not open for further replies.

texanman

Mechanical
May 21, 2008
37
I have been asked why not just duct-in some primary air (55-deg) from the central AHU into an IT room. I have specd out a Liebert, but owner wants to know why? I am looking for advise.
regards,
 
Replies continue below

Recommended for you

Because the IT room will have a constant high cooling demand. The adjacent office space will have variable cooling/heating demands, therefore the central AHU will be controlled by the small IT room and potentially over-cool the office or result in significant inefficient reheat. IT rooms also require 24/7 cooling.

Stick to the dedicated IT room Liebert unit as it the right design!
 
Assuming you can control the IT room from the main building air, the best reason is the 24/7 operation. To operate the entire building systems for an IT room outside the, perhaps, 14 hours a day plus 24 hours on each weekend is not very cost effective unless the whole building is 24/7.


Don Phillips
 
and you could add if I may, future expansion, they keep throwing all kinds of new racks in there every day.
I recall an IT room we designed, the tonnage was absolete by the time it was installed, the load tripled.
 
Sounds like a couple of switches and a patch panel kind of cupboard, but another good reason for a dedicated crac unit is to maintain the humidity spec. Electronics sans people is a dry load which has a high sensible heat ratio, which needs to be matched by the equipment. A normal unit would tend to dry out the space leading to static problems.
 
Thanks Guys, I think now I have good amo to reply to this issue.
 