- Jul 13, 2010
- 7
An installed transformer vault has 4 1000kVA transformers 13.8kV - 480V. The utility rates this installation at 200kAIC and (145, j1385) uOhms. There are a couple of issues I am having with this.
1) Why don't the Utility ratings and the xfrm ratings match? Assuming 5% impedance on the xfrms (is this a reasonable assumption?), the short-circuit current of 4 1000kVA is 96kAIC, correct?
2) The Utility will not accept current-limiting fuses as a means of reducing the kAIC ... Why?
1) Why don't the Utility ratings and the xfrm ratings match? Assuming 5% impedance on the xfrms (is this a reasonable assumption?), the short-circuit current of 4 1000kVA is 96kAIC, correct?
2) The Utility will not accept current-limiting fuses as a means of reducing the kAIC ... Why?