Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

khrone magnetic flow ( error ) 1

Status
Not open for further replies.

maher81

Industrial
Nov 12, 2012
1
Hi all,

I face a problem in KHRONE manetic flow transmitter, ( application error ).
But i don't know what is the actual reason for that.because it appears to me suddenly ( i am in commissioning so this pipe line is empty ) , has it relation with my status?
Because when this line has flow this message would be gone?

Thanks in advance,

Maher
 
Replies continue below

Recommended for you

Asked the manufacturer yet?

TTFN
faq731-376
7ofakss
 
Typical electromagnetic flowmeters do not work when the line is not fully flooded or has entrained gas. Most likely this is where your error is coming from. You should read the manual.
 
Magnetic flow meters typically require a pipe full of flowing liquid. This is probably where your problem lies. Magflow meters are also restricted to liquids where conductivity is at sufficient levels to induce measurable voltage but hopefully thisis not an issue
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor