Thedroid
Electrical
- May 18, 2008
- 196
I just replaced one of the DC drive motors on a cement kiln, and now there seems to be some sort of unbalance going on. The kiln is driven by two 75hp DC motors wired in series to an ABB DCS 500 controller. Power is transmitted through toothed Gates power belts, gear box, and a dual pinion, girth gear arrangement. The motor was replaced during an annual shutdown and other areas of the kiln were worked on at the same time, so the motor was not the only thing replaced.
We think that there is an uneven buildup of coating causing the torque requirements to be inconsistent. This was verified by a 200 degree difference in surface temp around the outside of the kiln.
As I watch the kiln turn it seems like the motors are passing the load back and forth and causing alot of noise and vibration for half a revolution. Measuring the armature current shows that there is not a linear increase in current as the heavier side is lifted, but more of a series of peaks and dips as the drive belts go slack and then tighten up again. Watching the voltage panel meters inside of the drive rooms shows that as 1 motors voltage increases the others decreases, then they switch roles and the other motors voltage increase and back and forth. Everyone is convinced that the problem is purely mechanical, but I'm not sure. I've never worked with DC motors in this configuration before, so I'm trying to understand what could be happening. Armatures and fields are wired in series.
We think that there is an uneven buildup of coating causing the torque requirements to be inconsistent. This was verified by a 200 degree difference in surface temp around the outside of the kiln.
As I watch the kiln turn it seems like the motors are passing the load back and forth and causing alot of noise and vibration for half a revolution. Measuring the armature current shows that there is not a linear increase in current as the heavier side is lifted, but more of a series of peaks and dips as the drive belts go slack and then tighten up again. Watching the voltage panel meters inside of the drive rooms shows that as 1 motors voltage increases the others decreases, then they switch roles and the other motors voltage increase and back and forth. Everyone is convinced that the problem is purely mechanical, but I'm not sure. I've never worked with DC motors in this configuration before, so I'm trying to understand what could be happening. Armatures and fields are wired in series.