Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Kinder Morgan, Inc. Natural Gas-Fueled Explosion and Fire; August 15, 2021; Continuation

Status
Not open for further replies.

FacEngrPE

Mechanical
Feb 9, 2020
1,643
thread815-486348 was closed, this is a continuation.
On August 15, 2021, about 5:29 a.m. local time, pipeline (line) 2000, a 30-inch diameter natural gas transmission pipeline owned and operated by Kinder Morgan, Inc. (Kinder Morgan) ruptured in a rural area in Coolidge, Arizona.
NTSB Opens Public Docket for Coolidge, Arizona Pipeline Rupture Investigation, Sept. 15, 2022 LINK
Screenshot_from_2022-09-18_17-10-50_sprmm7.png
 
Replies continue below

Recommended for you

The linked article indicates the line was originally an oil pipeline converted to gas service. The failure was adjacent to the longitudinal weld . It is possible that the specification and QC requirements for oil pipes are not equivalent to that for gas pipelines- TBD. It is not clear if a "smart pig" could have detected a fault in the longitudinal weld after several years of accumulated deposits in oil service. 2 fatalities resulted from the fire.

"...when logic, and proportion, have fallen, sloppy dead..." Grace Slick
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor