I work for a utility group and had contractors perform Mag. curves on our 110KV post CT's with the following results:
CT ratio & Class - 1600/1200/1000/400/1A 1.0M - 10VA
''A''Phase Tap (8.23Ω) ''B'' Phase Tap (8.25Ω) ''C''Phase Tap 3.45Ω
X1-X2=240.37V X1-X2=239.57V X1-X2=40.32V X1-X3=606.81V X1-X3=601.27V X1-X3=103.26V
X1-X4=724.03V X1-X4=719.78V X1-X4=126.42V
X1-X5=956.51V X1-X5=957.84V X1-X5=176.57V
I contacted the maufacture regarding the knee point voltages & measured resistance of AB phases verses C phase and was told that,“If the core complies with its class then there is no issue regardless of the mag curve reading.
Mag curves are used to determine the knee voltage of PX cores, the metering cores could also have high knee voltages.”
They have indicated that the Mag curve results are not critical to the function of the metering cores (only relevant to protection cores) as long as the metering core is within the required class of accuracy.
Please comment/advise as to your thoughts on this.
Thanks
CT ratio & Class - 1600/1200/1000/400/1A 1.0M - 10VA
''A''Phase Tap (8.23Ω) ''B'' Phase Tap (8.25Ω) ''C''Phase Tap 3.45Ω
X1-X2=240.37V X1-X2=239.57V X1-X2=40.32V X1-X3=606.81V X1-X3=601.27V X1-X3=103.26V
X1-X4=724.03V X1-X4=719.78V X1-X4=126.42V
X1-X5=956.51V X1-X5=957.84V X1-X5=176.57V
I contacted the maufacture regarding the knee point voltages & measured resistance of AB phases verses C phase and was told that,“If the core complies with its class then there is no issue regardless of the mag curve reading.
Mag curves are used to determine the knee voltage of PX cores, the metering cores could also have high knee voltages.”
They have indicated that the Mag curve results are not critical to the function of the metering cores (only relevant to protection cores) as long as the metering core is within the required class of accuracy.
Please comment/advise as to your thoughts on this.