jmurph36
Structural
- Feb 8, 2019
- 26
In the attached file, I am showing a bracing connection that I am attempting to design. The connection is failing according to RISA Connection because the software is considering bending in the knife plate as well as a combined tension/compression and flexure interaction per Chapter H in the AISC Spec. The only force that is passing through the knife plate is axial load of 69.1 kips T/C from the HSS brace. I have never seen any textbook or design example that considers building in this type of arrangement. Does anyone agree with me that this is a tension/shear failure only in the plates? I ran through the numbers and if RISA is correct then the knife plate would have to be 1 3/8" thick to make the connection work and this just seems way too thick when the tensile strength of a PL 6 5/8" x 3/8" is 80.5 kips (LRFD).