Hi,
I have an L-Shaped swimmming pool. I have added a construction joint to break the pool into two separate structures because I am concerned about the re-entrant corner. One section will be 45'-0 long x 8 feet wide and the other section is 15'x15'. I am now detailing the construction joints in the slab and walls and would appreciate some comments on whether I should detail the joint as a complete contraction joint (no steel through the joint) or as a partial contraction joint with atleast 50% of the horizontal steel crossing the joint. I plan to have a waterstop at the joint and a 1"x1" min waterproofing sealant at the surface of the joint on the water side.
I am in a seismic zone (SDC D)
Thanks
I have an L-Shaped swimmming pool. I have added a construction joint to break the pool into two separate structures because I am concerned about the re-entrant corner. One section will be 45'-0 long x 8 feet wide and the other section is 15'x15'. I am now detailing the construction joints in the slab and walls and would appreciate some comments on whether I should detail the joint as a complete contraction joint (no steel through the joint) or as a partial contraction joint with atleast 50% of the horizontal steel crossing the joint. I plan to have a waterstop at the joint and a 1"x1" min waterproofing sealant at the surface of the joint on the water side.
I am in a seismic zone (SDC D)