ARLORD,
You probably remember reading my post on a previous thread that you started, if not here it is with somemore info in it:
I designed an aeration basin matching these dimensions (146-ft long x 50-ft width x 27-ft height). Since the L/H was greater the 2, for simplicity the wall will perform as a cantilever member, unless I restrict the top of wall. The basin had an immediate wall running parallel with the 146-ft, so placed a 6-ft wide walkway (strut) cross all three walls, at the center of the structure (T'ing across the 50-ft dimension) to brace the wall at top. I also used a 6-ft wide (acting as a beam framing into it strut) walkway around all perimeter walls. If did not do this the required flexure strength would be like #10 at 6-inches on center, to much to close at the base. The end result was a 30-inch thick wall at the bass with #9 dowels at 6-inches on center with vertical steel at 12-inches on center. I stepped the wall down to 20-inches just past mid height. I sized the wall base (thickness) for the shear load without the additional environmental load factor (concrete only, I did not use any steel for shear capacity) and the flexure steel as required by ACI 530 with the environmental load factor. Be careful with the expansion and construction joints locations, I think I used 1-EJ and 3-CJs.
Make sure you follow the requirements in ACI 530 for temperature reinforcement. And double up on the temperature reinforcement as the base of the wall for at least 4D to 6D (height) to prevent vertical cracking as the wall cures. The foundation for the basin was a 3-ft thick mat with piles at 10-ft on center each way.
Just a reminder: The design of the crack control reinforcement in both directions is based on ACI 530 with unfactored loads.
What I worked on is not the same scenario as yours, but you could always create (3) walks crossing the 100-ft dimension, support them at (3) locations to provide yourself a modification of what I did and you must use STAAD to simplify analysis with the walkways. This should reduce you moment requirement at the base, but you will still probably be at a 32 to 34-inch wall.
Hope this helps.
RMunoz III