AlaskanME
Mechanical
- Oct 19, 2015
- 18
Hello,
I wanted to get your thoughts on a task I am dealing with and make sure as an entry engineer I am asking the right questions before I continue to proceed.
Background:
We have an API 650 50,000 bbl water storage tank (110' x 30') built in 1967 that is used for firewater and all other facility water needs. The tank currently is freeze protected in the winter using a 40# internal steam coil using 400# letdown steam. When it was originally built the tank was also outfitted with a forced draft natural gas heater for freeze protection but I have no documentation on the heater or if it was ever used ( I know it hasn't been used in the last 20 years). The tank currently does not have insulation. For economic and operation concerns the plant wants to shut down its steam generation, so I am investigating multiple options to maintain the freeze protection @ around 40-42F.
Options:
Electric immersion heater
I wanted to get your thoughts on a task I am dealing with and make sure as an entry engineer I am asking the right questions before I continue to proceed.
Background:
We have an API 650 50,000 bbl water storage tank (110' x 30') built in 1967 that is used for firewater and all other facility water needs. The tank currently is freeze protected in the winter using a 40# internal steam coil using 400# letdown steam. When it was originally built the tank was also outfitted with a forced draft natural gas heater for freeze protection but I have no documentation on the heater or if it was ever used ( I know it hasn't been used in the last 20 years). The tank currently does not have insulation. For economic and operation concerns the plant wants to shut down its steam generation, so I am investigating multiple options to maintain the freeze protection @ around 40-42F.
Options:
Electric immersion heater
- insulate tank to reduce heat loss (this will create inspection issues)
Let tank freeze during the winter
- ensure no instrumentation, internals, or vents will be affected
- NFPA 22 requires ambient temperature control
recirculating type heater
These are the options I am considering right now. Doing some heat loss calcs will be my next step to see if insulating is the way to go and to size the heater.
Let me know if you have any thoughts.
installing electric heater would require demoing old forced draft heater and internal piping
Forced natural gas heat
-would need to find new heater and inspect current heater internal pipingLet tank freeze during the winter
- ensure no instrumentation, internals, or vents will be affected
- NFPA 22 requires ambient temperature control
recirculating type heater
- allows for online repairs and maint.
- can be natural gas or electric
Add agitator/mixer to tank to prevent freezing- Not sure how to quantify that this would be an option
These are the options I am considering right now. Doing some heat loss calcs will be my next step to see if insulating is the way to go and to size the heater.
Let me know if you have any thoughts.