I am designing a 25-ft tall structure for equipment inside of a warehouse. There are no windows or roll-up doors in the room where the structure will be located, therefore wind loading is not considered. Project is in SDC A, so seismic loads are very low. And no dynamic loads are expected from the equipment.
What would be the minimum lateral load to be applied to the structure for stability? I have found many opinions, from applying 10 psf wind to applying a lateral load ranging from 1% to 10% of the dead load - I am looking for a reference in IBC or ASCE 7-10
Also, if calculating the load as a percentage of the dead load - how would you apply it in the ASD load combinations? just replace "0.6WL" with "0.01DL or 0.1DL"?
What would be the minimum lateral load to be applied to the structure for stability? I have found many opinions, from applying 10 psf wind to applying a lateral load ranging from 1% to 10% of the dead load - I am looking for a reference in IBC or ASCE 7-10
Also, if calculating the load as a percentage of the dead load - how would you apply it in the ASD load combinations? just replace "0.6WL" with "0.01DL or 0.1DL"?