Lateral pressure from a concrete backfill
Awre
74
I have a gravity wall composed of concrete block, the total height will be about 40 feet.
The backfill at the bottom third of the wall will be filled with concrete for a width of 10 feet approximately.
For the stability calculations, I think I can assume some shielding from lateral loads because of the concrete mass behind the wall for sliding by friction.
Can I also assume some resistance against overturning because of the cohesion between the concrete backfill (after setting) and the wall? If yes, what is the approximate value for that cohesion?
I'd just design for the same loads as no backfill. How much and who are you going to save? A few bars? A couple of inches of concrete?
Note that also you're going to need to control the rate of pouring the concrete to limit its lateral fluid load.
A 40-foot gravity wall is a big wall. What type of system are you planning to use?
A drawing or sketch would help.
Size of the concrete blocks? 1m x 1m or blocks at 100mm thick.
Vertical wall?
Width? Do you mean depth ? - this is why we need a drawing as we can't see what's in your head, or screen.
Gabion walls are often angled backwards at ~ 7 degrees.