Lateral Support for Piles (UBC 97)
MJPeterson
1
I am presently working on the foundation design for a piperack. The project is located in a Zone 1 seismic area (UBC 97). UBC Sec 1807.2 states that "Individual piles caps and caissons of every structure subjected to seismic forces shall be interconnecetd by ties." The pipe rack is a standard 2 layer pipe racks 25' wide by 40' tall by 200' long. The columns are spaced at about 25 feet on center. The code seems to imply that I will need to run a grade beam (tie) between each and every pile cap of the pipe rack. Is this the correct way to interpret the code? Is there a more cost effective way to meet the code requirements? Analysis alone does not require these ties.
The exception to UBC 1807.2 allows for "other approved methods" if "equivalent restraint can be provided." If the soils near the surface are stiff/strong enough to provide lateral restraint (based on lateral passive resistance) for the top of the pier, this is often used as an "other approved method".