JIMEY

Structural
Feb 5, 2009
29
0
0
CA
I have a 5"x27" glulam beam (very slender) spanning 35'. The compression side of this beam does not have any lateral support, and as a result, the beam fails in bending. I've calculated that in order for this beam to work, the compression side needs to be laterally braced at third points along the beam. What I'm not sure about is how much load those braces need to be designed for. I can't find any guidance on how to determine the lateral bracing load for timber beams. I know that for steel beams, the lateral bracing load is based on a percentage of compression load in the flange (usually about 2%). But in the case of a glulam beam like this, there are no flanges, so I'm at a bit of a loss. Even if there were flanges, I'm not sure the same rule that works for steel would also be appropriate for timber. Any suggestions? Thanks in advance.
 
Replies continue below

Recommended for you

I've never calculated it for timber but also have never really thought about it
With timber typically being rectangular cross-sections I think your load-applying element usually also gives you support
But I've looked into our code for interest and have snipped the relevant bits below for you to take a look at

Effectively, it says that you don't normally need to calculate it, but here's a really complex looking way to do it if you want to

Good luck

Buckling_1_arb7wu.png

-----------------------------------------------------------
Buckling_2_ck9qwc.png

-----------------------------------------------------------
Buckling_3_vvupcq.png
 
The 2% rule is essentially a P-delta check to account for out-of-straightness and is appropriate for relatively straight steel members. It is not suitable for potentially wonky timber members.
 
Thank you all for your help. I think I found the answer I was looking for. Eurocode 5 Part 1-1 has a section 9.2.5.2 which gives the load that lateral bracing for timber members (including beams) should be designed for. But if anyone is still interested, I've attached a link to a sketch showing my exact situation.
 
 https://files.engineering.com/getfile.aspx?folder=347a72df-04d8-4636-bb7f-04ac813e310a&file=0749_001.pdf
It's a bit of a judgment call I suppose, but I think most engineers would consider the existing framing as providing acceptable lateral bracing of the glulam, despite it not being exactly at the top. I have trouble picturing the beam failing in lateral torsional buckling with that framing there. In terms of the buckling restraint force, I wouldn't normally calculate that, but if I did, I'd probably use 2% of the compression component of the moment.

Your sketch (for convenience):
Glulam_bracing_kw73a4.jpg
 