Gents,
I am looking to control Rh in 5000 cu/ft of air with air replacement changes every 4 hours(low air flow).
The temperature range is 85 F(98%Rh) to 120 F(20%Rh)
The High Rh(95%-90%) at lower temps 85 F to 100 F and lower Rh(75% -20%) at higher temps 100F to 120F.
I am using dry heat (fin tubes)to heat and was going to use steam sprays to add Rh. I need to know what to expect in lbs/hr use of steam to size steam boiler for jets.
I figure there is a formula for volume of steam to increase Rh by 1% per cu/ft of air at various temps.
Is there such a beast??
With the volume of air I think the heat added by the steam will be small enough not to affect the temp wildly.Also if I place many small jets along the lenght of the space the Rh will be somewhat uniform.
space is 7'X 7'X 98'==4802 cu/ft(5000)
Air will enter from floor many small holes (1/2" on 4" centers) and exit out 4 evenly spaced draw fans(5-20 cfm/fan w vfd)
Spray misters above floor plate at floor level spaced at 10'?? along center line. Two temp/Rh sensors (rototronic) at 30' spacing(to avg). Fin coil under floor plate with holes 1/2" plate(to help with uniformity)and walk on. Hot water heated 150F to 200F.
1 small supply air fan 20 cfm to 100 cfm w/vfd control
Space pressure control by slightly faster supply fan then exhaust fan with dp xmitter and controller.
space pressure +.05 to -.05 " H20
Thanks,Joe
I am looking to control Rh in 5000 cu/ft of air with air replacement changes every 4 hours(low air flow).
The temperature range is 85 F(98%Rh) to 120 F(20%Rh)
The High Rh(95%-90%) at lower temps 85 F to 100 F and lower Rh(75% -20%) at higher temps 100F to 120F.
I am using dry heat (fin tubes)to heat and was going to use steam sprays to add Rh. I need to know what to expect in lbs/hr use of steam to size steam boiler for jets.
I figure there is a formula for volume of steam to increase Rh by 1% per cu/ft of air at various temps.
Is there such a beast??
With the volume of air I think the heat added by the steam will be small enough not to affect the temp wildly.Also if I place many small jets along the lenght of the space the Rh will be somewhat uniform.
space is 7'X 7'X 98'==4802 cu/ft(5000)
Air will enter from floor many small holes (1/2" on 4" centers) and exit out 4 evenly spaced draw fans(5-20 cfm/fan w vfd)
Spray misters above floor plate at floor level spaced at 10'?? along center line. Two temp/Rh sensors (rototronic) at 30' spacing(to avg). Fin coil under floor plate with holes 1/2" plate(to help with uniformity)and walk on. Hot water heated 150F to 200F.
1 small supply air fan 20 cfm to 100 cfm w/vfd control
Space pressure control by slightly faster supply fan then exhaust fan with dp xmitter and controller.
space pressure +.05 to -.05 " H20
Thanks,Joe