Leading Power Factors

Status
Not open for further replies.

Geep

Electrical
Mar 10, 2005
2
0
0
GB
Does anybody know of any way of correcting leading power factors associated with computer rooms and UPS's
 
Replies continue below

Recommended for you

Install line reactors. You could also turn an induction motor nearby. This would be analogous to running a synchronous condenser in the case of a lagging pf.

William
 
Is it only leading power factor? There could be over voltage, Harmonics as well when Computers and UPS are involved? What is the UPS size / capcity/ Load? Single phase,3 phase 120 volts?