sider
Mechanical
- Nov 26, 2021
- 43
Can somebody clarify a little setting of a pressure testing based on standard EN 378-2? So, currently the heat pump units (R410A) we need to test have HP switch set on 40 bars, and safety valve on 41,5 bar (+- 3% opening, so possibly it is opened on 40,2 and 42,7 bar respectively). We are testing on 40 bars, and in the last months we had some issues with safety valves failing. From my understanding, EN 378 states that leak pressure test must be conducted on pressure equal or less then MWP. The MWP on the old units was set on 40 bars, however new units don't have MWP stated. How would you approach this issue? For me there are few question I would like to clarify?
1. If the MWP is not stated, do we need to use the table where we get MWP from saturation temperatures?
2. Can we remove the safety valve during testing?
3. Is the main point of EN 378 leak pressure testing to test the unit in the whole max range to the setting of HP?
4. Is it weird to you that settings of HP and safety relief are so close?
Thanks in advance
1. If the MWP is not stated, do we need to use the table where we get MWP from saturation temperatures?
2. Can we remove the safety valve during testing?
3. Is the main point of EN 378 leak pressure testing to test the unit in the whole max range to the setting of HP?
4. Is it weird to you that settings of HP and safety relief are so close?
Thanks in advance