This is quite specific, but does anyone have any experience specifically to code of seemingly conservative estimates of bolt shear strength, where mortar is used?
This is specifically in clause 6.2.2.3 in BS EN 1992-4:2018:
6.2.2.3 Shear loads with and without lever arm
(1) Shear loads acting on fastenings may be assumed to act without a lever arm if all of the following conditions are satisfied.
a) The fixture is made out of steel and is in contact with the fastener over a length of at least 0,5 ⋅ tfix .
b) The fixture is fixed:
1) either directly to the concrete without an intermediate layer; or
2) using a levelling mortar with a thickness t grout ≤ 0,5d under at least the full dimensions of the fixture on a rough concrete surface (see EN 1992-1-1:2004, 6.2.5) as intermediate layer; the strength of the mortar shall be at least that of the base concrete but not less than 30 N/mm2.
This essentially means if you use any leveling mortar of any significant thickness, you will induce bending into your bolts, and with any shear loading, stresses that will result in using large bolt sizes. This seems extremely conservative, when a high strength mortar will provide continuity from the concrete platform.
Is this clause just absurdly conservative? Would be interesting to hear a wider viewpoint.
Liam
This is quite specific, but does anyone have any experience specifically to code of seemingly conservative estimates of bolt shear strength, where mortar is used?
This is specifically in clause 6.2.2.3 in BS EN 1992-4:2018:
6.2.2.3 Shear loads with and without lever arm
(1) Shear loads acting on fastenings may be assumed to act without a lever arm if all of the following conditions are satisfied.
a) The fixture is made out of steel and is in contact with the fastener over a length of at least 0,5 ⋅ tfix .
b) The fixture is fixed:
1) either directly to the concrete without an intermediate layer; or
2) using a levelling mortar with a thickness t grout ≤ 0,5d under at least the full dimensions of the fixture on a rough concrete surface (see EN 1992-1-1:2004, 6.2.5) as intermediate layer; the strength of the mortar shall be at least that of the base concrete but not less than 30 N/mm2.
This essentially means if you use any leveling mortar of any significant thickness, you will induce bending into your bolts, and with any shear loading, stresses that will result in using large bolt sizes. This seems extremely conservative, when a high strength mortar will provide continuity from the concrete platform.
Is this clause just absurdly conservative? Would be interesting to hear a wider viewpoint.