Wfg42438
Electrical
- Apr 10, 2017
- 70
I have seen some discussions about considering the zero-seq magnetizing current for secondary side fault of a XFMR with Wye grounding on the primary and y solid grounding on the secondary.
I am curious if anyone knows any good references that goes into an example calculation for the LG fault current for such as case?
For example, if i have the simple system below.
[URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1696040216/tips/2023-09-29_19-03-19_gcapxp.tiff[/url]
I took a stab at it and came up with the following assuming all quantities below are per unit.
Positive, Negative and Zero Seq impedances for the Utility as : Z1_U, Z2_U, and Z0_U
Positive, Negative and Zero Seq impedances for the Cable as : Z1_C, Z2_C, and Z0_C
Positive, Negative and Zero Seq impedances for the ZFMR as : Z1_XFMR, Z2_XFMR, and Z0_XFMR, then i also have the magnetizing XFMR zero seq impedance as ZMag_XFMR
Zpos=Z1_U + Z1_C + Z1_XFMR
Zneg=Z2_U + Z2_C + Z2_XFMR
The zero seq impedance is the part im not 100% sure on
From my understanding there is no zero seq flow on the primary
So the Utility and cable wont be in the picture just the XFMR zero seq impedance and the magnetizing zero seq impedance.
Therefore: Zzero= Z0_XFMR in parallel with ZMag_XFMR
If i want the LG zero Seq current at the secondary of XFMR T1 would i simply say:
3I0= (Vpf)/ (Zpos + Zneg + Zzero)
If someone can please help point me in the right direction i would really appreciate it.
I am curious if anyone knows any good references that goes into an example calculation for the LG fault current for such as case?
For example, if i have the simple system below.
[URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1696040216/tips/2023-09-29_19-03-19_gcapxp.tiff[/url]
I took a stab at it and came up with the following assuming all quantities below are per unit.
Positive, Negative and Zero Seq impedances for the Utility as : Z1_U, Z2_U, and Z0_U
Positive, Negative and Zero Seq impedances for the Cable as : Z1_C, Z2_C, and Z0_C
Positive, Negative and Zero Seq impedances for the ZFMR as : Z1_XFMR, Z2_XFMR, and Z0_XFMR, then i also have the magnetizing XFMR zero seq impedance as ZMag_XFMR
Zpos=Z1_U + Z1_C + Z1_XFMR
Zneg=Z2_U + Z2_C + Z2_XFMR
The zero seq impedance is the part im not 100% sure on
From my understanding there is no zero seq flow on the primary
So the Utility and cable wont be in the picture just the XFMR zero seq impedance and the magnetizing zero seq impedance.
Therefore: Zzero= Z0_XFMR in parallel with ZMag_XFMR
If i want the LG zero Seq current at the secondary of XFMR T1 would i simply say:
3I0= (Vpf)/ (Zpos + Zneg + Zzero)
If someone can please help point me in the right direction i would really appreciate it.