Delagina:
What ever you do, don’t give us any of the real engineering design info., that would let us hone-in on some of the important parts of the problem. Some dimensions, loads, member sizes, etc. really help us to visualize the real problem. Otherwise, you have one guy guessing and expounding on a 1 kip load and the next guy is talking about 1000 kips and 36 WF side sills/skids, and they are all just guessing and talking past each other. In any case, the hole in your WF web will probably not be a round hole with a doubler pl., those don’t take to slings very well. It will more likely be a 2 or 3" high, by 8 or 10" long slotted hole which will take and load the sling better. Then, take a 7 - 9" long piece of 4 or 5" dia. std. pipe and cut it longitudinally into quarter sections to be used as edge softeners on your slotted holes. You do have to be able to get in under the top flg. to weld these edge softeners to the WF webs. I don’t go out of my way to design tripping or unsafe features into my structures, but are we designing walkways or equip, skids here? I’ve never seen a skid that you couldn’t trip on or fall off of, and hurt yourself, if you are not careful, but they do have to be lifted.