SrChemE

Chemical
May 6, 2016
54
Hello!
I have some questions regarding the requirements on lifting levers for relief valves as it applies to a project I am working on.
The relief device in question features a packed lifting lever. The devices intent is to protect a positive displacement pump and its piping system from a blocked outlet scenario. The vessels that receive the fluid from this pipe are not pressure vessels. They do not operate above 15psig. The fluid in the system is 20 wt% caustic at 122F.

The code does not indicate the purpose of the lifting device in Section VIII. Section I mentions the lifting device being used to verify that the device is free to lift. This would however require that there be a task to open these valves before or shortly after putting a pump online or on some set inspection frequency.

Does this relief valve require a lifting device per code?

Is it sound reasoning to say that lifting devices on PSVs are only required by code on relief valves intended to protect vessels governed by ASME Section VIII and Section I?

Many thanks,
Sara
 
Replies continue below

Recommended for you

Not on 20% caustic. In general, lifting levers are required on steam, water, and air.

Good Luck,
Latexman
 
FYI: ASME VIII only requires lifting levers if the PRV is to be Code Stamped and is exclusively on steam, air or water (water above 140°F / 60”C). This rule need not be followed if the user desires to apply Code Case 2203 not to have levers.

*** Per ISO-4126, the generic term 'Safety Valve' is used regardless of application or design ***

*** 'Pressure-relief Valve' is the equivalent ASME/API term ***
 
Also, there is no pressure vessel here, soASME VIII doesn’t apply. You are better off looking at the pipe design code for protection requirements. I very much doubt a lifting lever is required.
 