Light Fixture Hangers 1

Status
Not open for further replies.

tft2001

Civil/Environmental
May 10, 2009
34
I am in the process of evaluating light fixture hangers that are ~10 to 20 years old. Is there a particular code and/or design standard associated with the evaluation of existing hangers or the requirements for new hangers (i.e., material, safety factors, etc.)?
 
Replies continue below

Recommended for you

Check capacity of anchors and rods versus weight of lights - pretty straight forward. NOW - throw seismic at it. That might get a bit challenging.
 
Thanks. I plan on performing exactly that, however, I am wondering if there is a particular code/standard that indicates what minimum strength/safety factor the anchor/hanger system is to comply with. Any suggestions?
 
Let me see if I can find something on that. Not sure if it is an actual code or not but I was actually pricing fixtures/hanging methods the other day for a project and they had recommended cable/chain values based on the weight of the fixtures. I was looking at gripple hangers though.
 
It doesn't look like they have any actual codes associated with them from what I can see but for the gripple wire hangers it has safety factors for the size and weight.
Gripple Hangers
or here was the local vendors verison
BLine Gripples

sorry if it doesn't answer your question but maybe it's a start?
 
Many anchors are rated at ultimate load. So be careful.. You should put a 4:1 or usually a 5:1 Safety factor on those numbers
 
Great! Appreciate all the comments.
 