I am working on a 4 story wood building where the owner has requested the wood shear walls be designed without OSB sheathing using light gauge x straps. This seems like feasible option but I have a few concerns.
1. The connection of the strap to the wood wall would be the hardest thing to work out. I can only get about 150 lbs in a nail and I need to develop 2.5 kips. Not to mention how do I transfer the lateral force back into the bottom plate of the wall.
2. I am in seismic design category C. What R value do I use?
If anyone has any experience using this type of system I would like to hear from you about your design approach and any field issues you encountered during construction.
Thanks