Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Lightening Arrester Rating

Status
Not open for further replies.

RIA123

Electrical
Aug 22, 2008
8
Guys – Need your help in selecting right sized Lightening Arrester.

I have to select an L.A. for the Primary of a substation transformer which has delta connected Primary at 115 kV. This substation transformer 115kV, Delta-Primary/ 23kV Secondary Y-solidly grounded, is being fed by a utility transformer (approx. 8.5kM away) 115kV, Y-solidly grounded secondary.

My question is – will I choose the L.A. based on delta winding (substation tfmr) or based on solidly grounded utility transformer?

Appreciate your comments.

Regards
 
Replies continue below

Recommended for you

Is there a source on the LV of the transformer? If not, then I'd size as a grounded system, if not then I'd be considering whether I could inadvertently be backfeeding an ungrounded system.
 
Thanks mgtrp
There is no source on the LV side.
Could you please explain the concept of a source on LV side influencing the LA selection criteria?. Also how does the backfeeding an ungrounded system affect the LA rating?.I was trying to select it on the basis of MCOV rating based on the grounding conditiones of the system.
Regards
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor