EE_NE

Electrical
Sep 4, 2021
3
0
0
US
Good evening,

I'm a new EIT and I'm dealing with a situation and would like some thoughts/feedback involving a 13.8kV delta -4.8kV delta substation and failing lightning arresters, specifically on the low-side of the transformer and the arresters on the out-going feeder distribution. The low-side MCOV rating of the arresters that are failing are 5.1kV. By our typical LA application guide, for a 4.8kV delta system, we are supposed to be using 5.1kV MCOV rated arresters. The LAs had failed last year, and were replaced by the 5.1 MCOV rating and those newly installed LAs failed again recently.

Digging into this a bit deeper, a recommendation was made to upsize the lightning arresters, but I feel that the problem (root cause of what is causing the LAs to fail) is not being addressed here. Related to this, a comment was made that there was an active ground on the ground detection analog meter.

1) Any recommendations for me to investigate to see what is going on?

2) Does the active ground mean there may be improper ground-grid at the station, and/or something on the distribution circuit(s) that may be the root cause as to why the LAs are failing?

2) There is currently no way to replace arresters on the out-going feeder lines without bringing a mobile transformer in, any thoughts on how to remedy this?

First post here - thank you in advance.
 
Replies continue below

Recommended for you

It seems your 4.8kV system is ungrounded.
No trip takes place on grounding of one of the outgoing feeders in an ungrounded system. The operator is supposed to have a procedure in place to identify the faulty feeder and isolate quickly.
If this is neglected or delayed, the system with single ground fault in place experiences repeated over voltage transients which could damage the Lighting Arresters (could damage the equipment / cables etc. which is worse).
I have seen this happening in my country and I suspect this happening in your 4.8kV system.
 
From the data given, your SA are selected properly for your 4.8kV DELTA system. For any delta ungrounded system there
should be a ground fault detecion & indication system to alert the operator. Because you cannot allow
the ground fault to continue indefinitely due to transient overvoltages. The other equipment on the same 4.8kV system
are also subjected to these transient overvoltages.
Therefore, my recommendataion is unless & until you install a ground fault detection/ indication system,
your SAs will continue to fail.
You have mentioned that your 13.8kV system is also DELTA. How do the SA on that side are surviving?
 
RRaghunath
Yes the 4.8kV is ungrounded - I will look into the neglection/delay for the operator to respond appropriately to faulty feeders.

Kiribanda
I will dig deeper into the detection system and see what is going on with it. The SAs on the 13.8kV side have survived thus far, field has not noted issues with them.
 
For your arrestors I’m not understanding why they can’t be replaced without installing a mobile.
I’m assuming these are station class arrestors. 4.8kV shouldn’t be a problem to change out hot.
Put the new ones on with HL clamps. That way you simply take them offline with a shotgun stick.
 
Kiribanda,
Quote "You have mentioned that your 13.8kV system is also DELTA" Unquote
The OP mentioned that 13.8kV side of 13.8/4.8kV transformer is Delta connected, as such there is no mention about the type of earthing for 13.8kV system.
It is possible that 13.8kV system is resistance earthed.
 
You might want to consider if your configuration warrants using a 6 arrester arrangement. See the attached ABB—APPLICATION NOTE 1.3 Arresters between phases. Overvoltage protection - which should apply generically regardless of the brand of arrester used.

None of this will help much until after the active ground is repaired.

The active ground can be anywhere in the distribution system. If you converted to a grounded system an active ground would blow the distribution fuse of the affected feeder or device.
 
 https://files.engineering.com/getfile.aspx?folder=520909e3-ed50-4aff-a3b9-9c90f69b1806&file=ABB_AppNotes_1.3_1HC0138869_EN_AA.pdf
Thank you all for the responses, digging into it.

Palletjack
"For your arrestors I’m not understanding why they can’t be replaced without installing a mobile." - the ones in this scenario are bolted onto the structure, would need to de-energize the line here?
 
Also, ungrounded 3-wire 3-phase systems that have no transformer + light bulb ground detector or similar means to drain direct current from the system can build up EXPLOSIVE amounts of static electricity during rain if there is any amount of overhead line. At 1 factory where they had 480 volts ungrounded a 600-amp motor circuit blew up right in front of me during a rain storm and that was the only place where lightning was heard. It does not matter what the voltage is whether it is 240, 480, or 4,800 volts. Low energy lightning can do a lot of damage. A cable plant technician for Ohio Bell told me that 97% of lightning damage to outdoor telephone cables comes from silent lightning or invisible lighting. Telephone cables have to be able to carry 300 VAC so that they can carry 105 VAC ringing current and so that they have an insulation level that is protectable to some extent. THWN wire is essentially a 600-volt building wire version of telephone wire. As the voltage goes up you will have smaller percentages for low level lightning damage but it will still be a lot.

There are some things you can use:

1. Convert the system to solidly grounded using a zig-zag set or a wye delta transformer with the wye side connected to your 4.8 KV distribution. The delta side would be corner gvrounded with nothing else connected. Either way you need to use 4 current transformers 2 of them in 1 of the phases so that they can be subtractively in pairs to 2 fault relays to protect the zig-zag set or other grounding transformer from internal faults. THe CTs for the A and B phases would be subtractively connected to 1 relay the other B phase and the C phase CT connected to the other relay. The 2 differential fault relays need to have a long time ( overload ) setting, a short time, and an instantaneous setting with the last setting above the inrush current of the grounding transformer. You also need to protect the grounding transformer from overload such as a CT in the comon ground wire or 3 relays using 3 of the first 4 CTs.

2. You could convert this system to resistance grounded. The 3 voltage transformers for monitoring the voltage to ground of each phase should be rated 7,200 volts at system frequency so that you can impose a 2.5 hertz 10 volt subsonic tracing tone that is compatible with the Merlin Gerin Vigilohm system or the Megger Geolux system. Each transformer 120-volt secondary would need to be connected to a 130-volt indicator lamp, a direct reading voltmeter, and if you want a voltage sensor that sends the voltage reading back to your dispatching center. The former system is the only one that offers both permanently mounted and portable transmitters and receivers and the Geolux system using portable transmitters and receivers only. You would need to build a heftier than stock subsonic transmitter using say a 140-volt "direct current" pulse width modulated servo drive to generate a 100-VAC subsonic tracing tone 2.5 Hertz or 5 Hertz. You would also need a parallel resonant 50-Hz or 60-Hz blocking device in series with the servo amplifier output plus a damping resistor. I do not remember if the Geolux system will receive 2.5 Hertz but I do remember that it can receive 5 Hertz.

You will also need 3 7,200-volt primary 240-volt secondary transformers connected in the wye primary broken delta secondary configuration. The 7,200-volt primaries would each be connected from each phase to ground. The 240-volt secondaries would then be connected in the broken delta configuration and neutral grounding resistor across the 2 open ends of the secondary. The secondary resistor needs to be able to withstand 720 volts continuously from a heat dissipation standpoint e.g. three 240-volt heating elements connected in series. There are different formulas for sizing the transformers and resistors to damp out voltage excursions.

ON this system you should run an overhead ground wire over the 4,800 volts close to and over the substation to help absorb lightning. You need to sink the ground rods as deeply as possible. See US Patent 8,439,125 for directions on how to do this plus some articles by Martin Conroy wrote on what he and the patent holder Richard Teebken did when their company Grounding Perfection was in business. Remember, a lightning arrestor will only be as good as its ground. This applies whether your system is solidly grounded or resistance grounded.

3. You could also do a delta to wye voltage raise to 4,800Y8,320 volts solidly grounded. Along New York 17 right before or after the Pennsylvania/New York line there are 3 4,800:4,800-volt power transformers that step down to 4,800 delta from 4,800Y8,320 volts. That was back in 1989 - the location could have been moved or the rest of the circuit voltage raised. That is, some power companies have both voltages.

4. You could also do a raise to 13,800 volts. Apparently your 13,800-volt system does not have sustained overvoltages that are blowing out the lightning arrestors. If the source is 7,970Y13,800 volts lime on Cleveland Public Power you can start installing dual voltage transformers and a Protective Earth neutral conductor on the 4,800-volt system. I have seen dual voltage transformers of these voltages:

4,340x7,620 volts single phase and 4,340 delta x 13,200 delta on Cleveland Electric Illuminating Company.
4,800x7,620 volts single phase on the Holmes-Wayne power cooperative.
A photo of a 4,800x16,000-volt single phase on a Canadian electric utility.
2,400x7,200 volts single phase and 7,200x13,200 volts single phase on Ohio Edison.

A 4,800x7,970 volt or a 4,800x13,800-volt single phase transformer is theoretically possible.
 