We are getting wrote up for hooking up lightning arresters wrong. The engineer wants the bottom to go to the pole ground. All 3 straight to pole ground. The old way was to hook 3 together, than take each one to the system neutral. What are your thoughts. Thank you, Bob
 
Replies continue below

Recommended for you

What are you protecting? If protecting an underground cable, connect to the cable shield. If a transformer, connect to the transformer tank. Best protection occurs when the lead length on both sides is kept as short as possible. Rules 1 and 2 also apply.
 
They are on utility poles, 5 sets per mile. Thank you, Bob
 
Then you are simply protecting the aerial insulation against flashover. Is this a multi-grounded system with a low neutral? If so, run the pole ground conductor up past the neutral to pick up the arrester ground leads, bonding the neutral where it passes. I see no point in separately jumpering the arresters together.
 
Thank you, that answers my question. Bob
 
I would agree with Stevenal. That is the way my utility does it and I would suspect the majority of utilities do it.
 
As a distribution lineman for many years, we have always used, or installed a pole ground and bonded at the neutral, than installed a ground wire on the under side of the cross arm for the ground side of the arresters. this allowed for a short jumper wire from the line to the top of arresters. And also best to use compression type connectors, and split bolts
[atom]
 
We use a bracket for both 3 phase and 1 phase. We are a Cooperative, so we make a circle ground or have 2 points were it is grounded. Thank you, Bob
 
Im not sure of your jurisdiction, but NFPA 780 requires the downconductors to go directly to a pole ground. And they should ideally be in a symmetrical configuration, for ex., on diagonally opposite corners of a building or transformer. And then as baaman said, circle ground or two points grounded or ground ring, or radial grounds are also allowed.
 
We're speaking of arresters, not lightning rods. Try IEEE C62.22 for an applicable US standard.
 
Split bolts have a habit of working themselves loose, so we will no longer use them here my utility for any grounding application.
 