JohnMcNutt
Industrial
- Mar 3, 2013
- 111
Folks,
I have been tasked to develop some kind of a solution for a problem of an off grid solar/inverter system sustaining repeated lightning damage. Probably to the charge controllers although that is not 100% known to me.
This is a standard off grid system, by standard I mean (have not visited the site personally, but this is how it was described to me) ~300 watt panels maybe 10-30 of them on a ground mounted metal frame out on some rocky point, hooked in series up to a voltage of about 250 VDC and then run a couple hundred feet underground to a room where there are Midnite/Outback charge controllers, some ~30 kWh of lead-acid batteries and an Outback inverter setup.
They probably have some Midnite SPDs which are basically some relatively small MOVs in a box at either end.
I have been tasked with this because I am also an RF guy and I see that RF sites with standard Polyphasers can take direct hits and be undamaged over many years, but they all operate at DC ground.
The problem as I see it here is that we don't have the luxury of anything being DC grounded since it is supplying DC power. So lightning strikes on/near the array, raises the potential of the metal frame of the array to several kV, this overcomes the insulation resistance of the solar modules, and current flows back on the positive lead and again overcomes insulation resistance on a charge controller and damages something along the way.
I wonder if the MOV Midnite SPDs are too little, too late.
I can think of three solutions:
1. Increase PE conductor size, possibly even ABOVE power conductor size, so the voltage of the array, voltage of the metal objects back in the inverter shed, batteries, etc. all raise in potential in lock step and lightning current does not flow on any normally power-carrying parts, especially semiconductors.
2. Source and install MOVs or some other type of arrestor that reacts faster, shunts more current, or both.
3. Install some sort of inductance on the positive power lead. Unknown effect on the charge controllers if they quickly try to stop incoming current flow as part of normal operation. Perhaps a hefty Zener diode and/or capacitor beyond the inductor would be prudent. This is a stretch but I know that Polyphaser is big on LC networks these days instead of gas discharge so I wonder if it could be scaled up for this application. A bit of a stretch I am sure.
Thoughts?
I have been tasked to develop some kind of a solution for a problem of an off grid solar/inverter system sustaining repeated lightning damage. Probably to the charge controllers although that is not 100% known to me.
This is a standard off grid system, by standard I mean (have not visited the site personally, but this is how it was described to me) ~300 watt panels maybe 10-30 of them on a ground mounted metal frame out on some rocky point, hooked in series up to a voltage of about 250 VDC and then run a couple hundred feet underground to a room where there are Midnite/Outback charge controllers, some ~30 kWh of lead-acid batteries and an Outback inverter setup.
They probably have some Midnite SPDs which are basically some relatively small MOVs in a box at either end.
I have been tasked with this because I am also an RF guy and I see that RF sites with standard Polyphasers can take direct hits and be undamaged over many years, but they all operate at DC ground.
The problem as I see it here is that we don't have the luxury of anything being DC grounded since it is supplying DC power. So lightning strikes on/near the array, raises the potential of the metal frame of the array to several kV, this overcomes the insulation resistance of the solar modules, and current flows back on the positive lead and again overcomes insulation resistance on a charge controller and damages something along the way.
I wonder if the MOV Midnite SPDs are too little, too late.
I can think of three solutions:
1. Increase PE conductor size, possibly even ABOVE power conductor size, so the voltage of the array, voltage of the metal objects back in the inverter shed, batteries, etc. all raise in potential in lock step and lightning current does not flow on any normally power-carrying parts, especially semiconductors.
2. Source and install MOVs or some other type of arrestor that reacts faster, shunts more current, or both.
3. Install some sort of inductance on the positive power lead. Unknown effect on the charge controllers if they quickly try to stop incoming current flow as part of normal operation. Perhaps a hefty Zener diode and/or capacitor beyond the inductor would be prudent. This is a stretch but I know that Polyphaser is big on LC networks these days instead of gas discharge so I wonder if it could be scaled up for this application. A bit of a stretch I am sure.
Thoughts?