Lightning protection of a 200 ft long pipe

Status
Not open for further replies.

kookypedia

Electrical
Jun 9, 2016
62
Guys,
I am trying to protect the following pipe against lightning. What is your suggestion?
1- To put air terminals every 50ft along the pipe
2- Using static mast at both ends of the pipe and running a wire along the pipe?
3- Any other suggestion?

lightning_f8o8sl.png
 
Replies continue below

Recommended for you

In my opinion, you may follow NFPA 780/2011 chapter:
7.3.2 Zone of Protection for Masts and Overhead Ground Wires. 7.3.2.6 Overhead Ground Wire.
One row of ground wire and supporting mats it is enough-if the pipe will stay in 30 m protecting radius.
It depends on wire material, wind and ice in order to calculate the maximum span. However 100 ft. in my opinion, it will be o.k.
 
The problem is that I have not seen protecting pipes in the past. May be they were all thick enough and grounded that we didn't ground them.
 
I agree with you. NFPA 780 states:
art.7.1.2.1 “Metallic structures that are electrically continuous; tightly sealed to prevent the escape of liquids, vapors, or gases; and of 4.8mm(3⁄16 in.) thickness or greater to withstand direct strikes in accordance with 7.3.2 shall be considered to be inherently self-protecting.”
However, if there is a flammable material involved, all appurtenances where flammable concentrations of vapor or gas escape to the atmosphere shall be closed or otherwise protected against the entrance of flame.
By-the-way, from art.7.3.2 important is the grounding method and end protection.

 