We are testing concrete for a project that requires 3500 psi lightweight concrete. We are not casting the samples, just picking up, lab curing and breaking. Our Coefficient of Variation for all other concrete on this job ranging from 2500 to 8000 psi is from 1.4 to 2.6 for which <3.0 is the best ACI rating. However the LW concrete has a variation of 6.3 for a total of 15 sets of 2 breaks @28 days. We are curing and breaking the same as all the other concrete. This "with-in" test variation is is a function of the lab and field casting and curing.
The suppiler Overall Std. Dev is 474 corrected for 15 sets which is Very Good even though the average strength is 3290
This material is being used as a parking garage topping and is being pumped multiple stories. The slump ranges from 7.5"-10.5" and air between 7.75% and 10% via Rolometer. But there is no clear trend between these and the strength.
ASTM C330 talks about ater curing for 7 days then floor curing for the remaing 21 days. But this is a standard specification and not meant for job site control.
The Oven Dry Density and Equilibrium Density has not been requested.
Any ideas on what to look for here to improve the testing?
The suppiler Overall Std. Dev is 474 corrected for 15 sets which is Very Good even though the average strength is 3290
This material is being used as a parking garage topping and is being pumped multiple stories. The slump ranges from 7.5"-10.5" and air between 7.75% and 10% via Rolometer. But there is no clear trend between these and the strength.
ASTM C330 talks about ater curing for 7 days then floor curing for the remaing 21 days. But this is a standard specification and not meant for job site control.
The Oven Dry Density and Equilibrium Density has not been requested.
Any ideas on what to look for here to improve the testing?