Good day protection engineers,
I am struggling to see how in the SEL 411L protection manual example they managed to convert the line primary susceptance values to secondary values. I understand the primary values are derived from line characteristics like impedance, capacitance, geometry etc and short circuit program can determine it.
We have the following :
Line length : 70 miles
CT ratio (at this end) : 1600:5A
VT Ratio: 500kV:111.11V
Line voltage : 500kV
Positive sequence susceptance : 0.009 mS/mile (primary).
So the total susceptance will be : 0.009 mS x 70 = 0.000 63 S.
When reflected to secondary, they obtained 8.86 mS. Can someone explain how they got this value please. I tried multiplying the primary value by the CT Ratio/VT ratio but seems wrong. Is there anything I am missing?
I am struggling to see how in the SEL 411L protection manual example they managed to convert the line primary susceptance values to secondary values. I understand the primary values are derived from line characteristics like impedance, capacitance, geometry etc and short circuit program can determine it.