bspace123
Electrical
- Sep 3, 2009
- 27
Hello
We have two line differential relays on two parallel cables supplying a 6.6kv switchboard. The diff relays are linked by fiber communication. The cable run lengths are 100m and 200m.
The switchboard supplies a bunch of DOL started 1Mw motors.
Whenever we start one of the motors, the differential relays trip on diff current. When we observe the waveform capture and events file from the relay sets, we notice a 60deg phase shift between phases (i.e a-a b-b c-c) on one cable and 30deg on the other. Although shifted, the phases remain 120deg apart and magnitudes are the same.
If we disable the diff prot, start the motors then re-enable they do not trip.
Seems to me like the phase shift is due to inductance in the cable, but 60deg is much more than I’ve ever seen on such cable run lengths. Cables are 2x3c 400mm2 CU in parallel.
Anyone have any other thoughts on why the phase shift is occurring ?
We have two line differential relays on two parallel cables supplying a 6.6kv switchboard. The diff relays are linked by fiber communication. The cable run lengths are 100m and 200m.
The switchboard supplies a bunch of DOL started 1Mw motors.
Whenever we start one of the motors, the differential relays trip on diff current. When we observe the waveform capture and events file from the relay sets, we notice a 60deg phase shift between phases (i.e a-a b-b c-c) on one cable and 30deg on the other. Although shifted, the phases remain 120deg apart and magnitudes are the same.
If we disable the diff prot, start the motors then re-enable they do not trip.
Seems to me like the phase shift is due to inductance in the cable, but 60deg is much more than I’ve ever seen on such cable run lengths. Cables are 2x3c 400mm2 CU in parallel.
Anyone have any other thoughts on why the phase shift is occurring ?