GWright303
Chemical
- Dec 1, 2008
- 7
I would appreciate comments on the following:
I am examining an existing emergency vent, (on a funda filter), to ensure its capacity is suitable for a fire case. The existing emergency vent line is 3", vents to a dump tank, and the Bursting Disc is set at 4 barg. This work is a HAZOP review action.
I have surveyed the existing line (length, bends etc)such that I can compare its capacity vs the calculated relief rate.
I have identified that the worst possible case for a fire to occur, would be during cleaning, when the filter is completely full of acetone.
Using API methods, and the equipment GA drawing, I have calculated the heat absorption as a result of the fire.
As the vessel (filter) is liquid full, the initial effect will be thermal expansion. Correspondingly, (in conjunction with the heat absorbtion from before), I have used the hydraulic thermal expansion equation (from API 521) to calculate the initial liquid relief rate, (as API 521 suggests on pg18), due to the liquid swell.
What I have calculated so far is the initial liquid relieving rate only. However, if heat input continues, and the acetone boils, then vapour generation would take over as the determining factor for relief sizing.
The bursting disc will pop at 4 barg. I need to determine what the temperature is at this point, so I can judge whether relief will be liquid only, or two-phase.
My question is - how?
I dont know if I have somehow missed a section, or whatever, (perhaps I am barking up the wrong tree?), but there seems to be zero guidance on this in the API documents. There is guidance re relieving temperatures in the case of vessels which are full of gas ("unwetted") but not for this case.
I would gratefully listen to any advice on this, as well as how I have approached the problem so far.
Thanks for reading.
I am examining an existing emergency vent, (on a funda filter), to ensure its capacity is suitable for a fire case. The existing emergency vent line is 3", vents to a dump tank, and the Bursting Disc is set at 4 barg. This work is a HAZOP review action.
I have surveyed the existing line (length, bends etc)such that I can compare its capacity vs the calculated relief rate.
I have identified that the worst possible case for a fire to occur, would be during cleaning, when the filter is completely full of acetone.
Using API methods, and the equipment GA drawing, I have calculated the heat absorption as a result of the fire.
As the vessel (filter) is liquid full, the initial effect will be thermal expansion. Correspondingly, (in conjunction with the heat absorbtion from before), I have used the hydraulic thermal expansion equation (from API 521) to calculate the initial liquid relief rate, (as API 521 suggests on pg18), due to the liquid swell.
What I have calculated so far is the initial liquid relieving rate only. However, if heat input continues, and the acetone boils, then vapour generation would take over as the determining factor for relief sizing.
The bursting disc will pop at 4 barg. I need to determine what the temperature is at this point, so I can judge whether relief will be liquid only, or two-phase.
My question is - how?
I dont know if I have somehow missed a section, or whatever, (perhaps I am barking up the wrong tree?), but there seems to be zero guidance on this in the API documents. There is guidance re relieving temperatures in the case of vessels which are full of gas ("unwetted") but not for this case.
I would gratefully listen to any advice on this, as well as how I have approached the problem so far.
Thanks for reading.