Liquid service for Pilot Safety Valve
Hansac
41
Can share on experience with using Pilot SV for liquid service (boiler feed water, operating at 200 barg and 160 degC). Set pressure is 250 barg. During start-up, sometimes there are pressure spikes above 95% set pressure, due to operational issue.
I'd like to hear similar stories (successful or otherwise), in terms of maintenance, inspection, and operation.
What exactly is the valve experiencing? You say that the pressure spikes, but how is the valve responding?
Do you have a specification sheet for the valve?
Moreso, can you advise on the size, rating and model no/manufacturer?
What is the history of the application? When installed, service data - part changeouts, earlier reported issues?
Inlet piping configuration? Photographs.
What is the code of the application (ASME I, VIII? etc.).
Pilot valves usually get you closer to the set point before discharge.
But if the pressure is spiking above 95-98% of set pressure then you need to solve the problem (the spiking) not the valve.
Otherwise you are normalising failure.
In any well designed and operated plant the Safety Valves ( the key is in their name), should NEVER lift unless their is some sort of operational or mechanical failure ( or a fire). But if this is happening regularly on start-up then something is not right and you need to fix it. I realise this is probably not what you came here looking for, but that's how I look at it.
any lifting of a Safety Relief valve should be treated as a serious failure incident and suitable investigations and recommendations / precautions taken to prevent it happening again. Accepting it as "one of those things" leads you down dark and dangerous paths. IMHO.