Can anyone tell (per NFPA) what is the maxium run length for liguidtight flexible nnmetallic conduit.
 
Replies continue below

Recommended for you


Here it is as per the Ontario Electrical Safety Code - 2003'

Rule 12-1302(2)

Runs of not more than 1.5 m of 3/8 (12) trade size liquid-tight flexible conduit shall be permitted for the connection of equipment.

Intent for Rule 12-1302(2). Since the 3/8 trade size conduit is not recognized as a general-purpose conduit raceway method, we intend that it be restricted in use to runs of not more than 1.5 m for the connection of electrical equipment.

 
Per NEC, I'm not aware of a maximum length. However, if an equipment bonding jumper is required and routed on the outside of the flex, the length of the bonding jumper cannot exceed 6 feet. This situation is typically encountered when a rigid steel conduit system is used as a grounding conductor (the el cheapo) and the flex is used for final connection to a motor. If you run a separate grounding conductor all the way back, this removes this length restriction, I believe.
 
per 2002 NEC 356.12(3): Uses not permitted, lengths longer than 1.8m (6 ft) except as permitted in 356.100(5) or where longer length is approved as essential for a required degree of flexibility.

 
except as permitted in 356.100(5)

That should have been 356.10(5)which refers to support 356.30 : every 900mm (3ft) and within 300mm (12") on every box,fitting,etc.
 
Crowbar1 is right - I missed the "nnmetallic" in the original question. My answer was for metallic flex.

Sorry for the confusion.

Dave
 