Literature on Sizing Zig-Zag Transformers for Large Scale Solar Farms connected to the Grid

Status
Not open for further replies.

dZ.Anthony

Electrical
May 30, 2022
1
Need literature references on Sizing Zig-Zag Transformers for Large Scale Solar farms connected to the transmission grid.
 
Replies continue below

Recommended for you

IEEE C57.159 (Photovoltaic systems)
IEC/IEEE C57.60076-16 (Wind systems)

Converting energy to motion for more than half a century
 
Most utilities require grounding transformers to satisfy their effective grounding requirement. However most utilities apply the X0/X1<3 and R0/X1<1 criterium to meet this requirement which is inconsistent with the recommendations of C62.96.6. Standard C62.92.6 has some further discussion on Effective Grounding in Section 8.1. In addition there is a report published by EPRI with some additional information titled Effective Grounding for Inverter-Connected DER. Good luck!